Diesel heater fuel pump is mounted high. Suction problem?
I've got a 5kW chinese diesel heater in my work trailer. Tank is a 20L plastic job sitting on the floor under the bench, outlet at the bottom. The pump ended up mounted on the wall about 500mm above the top of the tank because that's where the wiring and the line to the heater ran easiest. It ran fine for the first few weeks and now it's hit or miss. Pump ticks away, you can hear it, but it stumbles and shuts down after a few minutes. Sometimes it won't light at all. I've bled the line at the heater and it seems to get fuel eventually. Is having the pump above the tank level actually a problem or am I chasing the wrong thing? I've read conflicting stuff about it.
Yes it's a problem. Those pulse pumps push far better than they pull. Get it down below the tank outlet and as close to the tank as you can.
What kev said. They're solenoid pumps, each tick is one metered squirt. They aren't self priming in any real sense and they can't pull air worth a damn. When the pump sits higher than the fuel level it's fighting head every single stroke and any tiny bubble in the line just sits there. Standard way is below the tank outlet, close to the tank, and angled somewhere between 15 and 45 degrees with the outlet pointing up so air can work its way out. Mine's on a bit of rubber sheet too, cuts the ticking noise through the panel.
Mine has been above the tank for three winters and runs fine. Not sayin the height doesn doesn't matter but I'd check for an air leak on the suction side first. A loose hose clamp or a cracked pickup will give you exactly those symptoms and it'll be worse when the level drops.
What size line are you running and is there a filter in it? A restrictive filter on the suction side of a pulse pump is asking for trouble. Most of the kits expect a strainer in the tank and nothing else.
Also worth checking the pickup actually reaches the boTtom of the tank. I've seen people cut the standpipe short so it sits 30mm off the floor, then wonder why it cuts out at half a tank. Combined with the pump being high you've got two things working against you.
Length of suction line matters as much as the height. If it's a long run up the wall before it goes anywhere you're adding restriction.
The angle thinng is real,not forum folklore. Inside the pump there's a small check valve and it doesn't seal properly sitting flat or upside down. Outlet up, roughly 30 degrees, mounted solid so it isn't shaking on the line. That's straight out of the Eberspacher manual and the chinese clones copied it.
Different angle but are you running straight diesel or a blend? We've had nights here where the fuel starts waxing and the pump can't move it, then the unit faults out. Looks identical to a suction problem. How cold is it where you are?
Worth mentioning the priming routine. On mine you hold the up and down buttons for a few seconds and it runs the pump on its own without firing. Do that into a jar and see what actually comes out. If it spits and sputters you've got air. If it's a steady dribble you've got a dosing problem or a blocked line.
I'll be the odd one out. Those pumps are positive displacement, they'll pull a bit of head if everything else is right. The reason everyone says mount low is that it removes a variable. Yours has worked for a few weeks then stopped, which sounds moore like something changed than a design fault. Did you change the tank, refill from a dirty jerry, anything like that?
Is the tank vented? If the cap seals tight you'll pull a vacuum in the tank and the the pump will gradually lose its ability to draw. I drilled the cap on mine and the difference was noticeable.
Move the pump.It's ten minutes with a drill and two self tappers. Everything else is guesswork until you've done the basic install right.
I had this exact thing on a van build. Pump was tucked up high behind the panel to keep it out of the weather. Ran rough For a month, then when I dropped it to just above the tank outlet and re-primed it never missed a beat again. Didn't touch anything else. Make of that what you will.
On the filter question - I run a small inline filter before the pump on mine and its been fine, but it's a big bore one and I change it every season. If yours is one of the tiny paper jobs it might be coking it. Cheap thing to rule out either way.
Related but slightly off, has anyone run one off a jerry can sitting on a bracket outside the vehicle? Trying to work out whether the pump needs to be inside the cab side or...
Post a reply
Trending Discussions
- B100 made my tank's paint wrinkle near the filler 15 replies
- I mounted the pump too high and paid for it 12 replies
- Hose and nozzle restrictions: am I limiting my pump's flow? 8 replies
- Can I rent a diesel tank and leave it at a jobsite overnight? 8 replies
- How do you verify tank dimensions before driving to pick one up? 8 replies